• shdudns 8 hours ago |
    How is DC better than a three phase delta 800Vrms, at 400Hz?

    - Three conductors vs two, but they can be the next gauge up since the current flows on three conductors

    - no significant skin effect at 400Hz -> use speaker wire, lol.

    - large voltage/current DC brakers are.. gnarly, and expensive. DC does not like to stop flowing

    - The 400Hz distribution industry is massive; the entire aerospace industry runs on it. No need for niche or custom parts.

    - 3 phase @ 400Hz is x6 = 2.4kHz. Six diodes will rectify it with almost no relevant amount of ripple (Vmin is 87% of Vmax) and very small caps will smooth it.

    As an aside, with three (or more) phase you can use multi-tap transformers and get an arbitrary number of poles. 7 phases at 400Hz -> 5.6kHz. Your PSU is now 14 diodes and a ceramic cap.

    - you still get to use step up/down transformers, but at 400Hz they're very small.

    - merging power sources is a lot easier (but for the phase angle)

    - DC-DC converters are great, but you're not going to beat a transformer in efficiency or reliability

    • shiroiuma 8 hours ago |
      >- no significant skin effect at 400Hz -> use speaker wire, lol.

      What are you talking about? There's a very significant skin effect at 400Hz. Skin effect goes up with frequency. These datacenters use copper busbars, not cable, so skin effect is an important consideration.

      • shdudns 7 hours ago |
        At 100 000 A for a 100 MW data center at 1000 V, speaker wire is a joke.

        You obviously need at least a dozen stands in parallel!!

        Clearly skin effect scales with frequency but, 400 Hz is still low, only 2.5x lines frequency (the scale is by the root); so the skin depth is 3mm. 3mm on each side makes for a pretty hefty rectangular cross-section.

        • bigiain 6 hours ago |
          If you could get that 100,000Amps flowing through your speaker wire, the vaporised copper and the plasma channel would probably keep your 100MW flowing, at least until your building caught fire.
          • jacquesm 6 hours ago |
            Even your monster cable? ;)
            • bigiain 6 hours ago |
              Well, it'd still vaporise, but it'd sound smoother and more musical as it did it, and the soundstage from the plasma arc would be _stunning!_
              • jacquesm 6 hours ago |
                It's almost worth the experiment and your cables are a sacrifice I'm willing to make. For science, of course.
                • bigiain 6 hours ago |
                  You're _so_ right!

                  I'm pretty sure you have my delivery address from when I bought sorted Lego from you about 10 years back.

                  Let me know when to expect the 100,000Amp test equipment!

                  I shall make sure I wear better PPE than just my reading glasses.

                  :-)

                  • jacquesm 5 hours ago |
                    This would be the funniest thing to do. 100K Amps is doable, the question is for how long. That would be one very impressive bank of capacitors. And to turn a 00 into plasma would have some spectacular side effects, such as raining molten copper across a sizeable area. Just your reading glasses would indeed not be enough, there probably isn't any PPE that I would consider entirely safe other than sufficient distance from ground zero. But now I'm really curious. I have a spot welder that will do bursts of 5KA and that will happily throw the breaker every so many welds. 100KA sustained will be a fair engineering challenge.

                    Ah, that lego project... that was one I always wondered if I should have industrialized it but sourcing enough lego was a real problem.

                    • adiabatichottub 5 hours ago |
                      • bigiain 4 hours ago |
                        See also (as posted elsethread): https://www.youtube.com/watch?v=RoGbrgOhPes
                      • jacquesm 4 hours ago |
                        Holy crap. That's a whole series of bad ideas extremely well executed. That guy probably has never seen what a lead acid battery can do when it explodes. He keeps hiding away from the hot metal but in the path of ~half of those batteries. Ignorance is bliss.

                        That's low voltage lightning :)

                        • adiabatichottub 3 hours ago |
                          He was gifted an arch flash suit by the guys from Lightening on Demand :D
                          • jacquesm 3 hours ago |
                            "The gift of life". Complete madness.
    • adamking 7 hours ago |
      > no significant skin effect at 400Hz -> use speaker wire, lol

      now run that unshielded wire 50 meters past racks of GPUs and enjoy your EMI

      > The 400Hz distribution industry is massive; the entire aerospace industry runs on it

      nothing in that catalog is rated for 100kW–1MW rack loads at 800Vrms

      > 3 phase @ 400Hz is x6 = 2.4kHz... Your PSU is now 14 diodes and a ceramic cap

      you still need an inverter-based UPS upstream, which is the exact conversion stage DC eliminates

      > large voltage/current DC breakers are.. gnarly, and expensive. DC does not like to stop flowing

      SiC solid-state DC breakers are shipping today from every major vendor

      > DC-DC converters are great, but you're not going to beat a transformer in efficiency or reliability

      wide-bandgap converters are at 95%+ with no moving parts

      • shdudns 6 hours ago |
        "now run that unshielded wire 50 meters past racks of GPUs and enjoy your EMI"

        Multipole expansion scales faster than r^2.

        Also, im not in the field (clearly) but GPUs cant handle 2.4 kHz? The quarter wavelength is 30km.

        "nothing in that catalog is rated for 100kW–1MW rack loads at 800Vrms"

        Current wise, the catalog covers this track just fine. As to the voltages, well that's the whole point of AC! The voltage you need is but a few loops of wire away.

        "you still need an inverter-based UPS upstream, which is the exact conversion stage DC eliminates"

        So keep it? To clarify, this is the "we're too good for plebeian power, so we'll transform it AC->DC->AC", right?

        "SiC solid-state DC breakers are shipping today from every major vendor"

        Of course they do. They're also pricey, have limited current capability (both capital costs and therefore irrelevant when the industry is awash with GCC money) and lower conduction, and therefore higher heat.

        They're really nice though.

        "wide-bandgap converters are at 95%+ with no moving parts"

        transformers have no moving parts. Loaded they can do 97%+ efficiency, or 2MW of heat eliminated on a 100MW center.

    • prezk 7 hours ago |
      An advanced AI rack might use 100kW = 800V 125A, requiring gauge 2, quarter inch diameter---this isn't your lol speaker wire. Actually, I apologize, I realized I may be talking to a serious audiophile, didn't mean to disrespect your Monster cables.

      The skin depth by the way is sqrt(2 1.7e-8 ohm m / (2 pi 400Hz mu0))=~3mm for copper---OK for single rack, but starts to be significant for the type of bus bars that an aisle of racks might want.

      As for efficiency, both 400Hz transformers AND fancy DC-DC converters are around 95% efficient, except that AC requires electronics to rectify it to DC, losing another few percent, so the slight advantage goes to DC, actually.

      As for merging power, remember that DC DC converter uses an internal AC stage, so it's the same---you can have multiple primary windings, just like for plain AC.

      • bigiain 6 hours ago |
        > I realized I may be talking to a serious audiophile, didn't mean to disrespect your Monster cables.

        I am a recovering audiophool.

        I do own a pair of 2m long Monster Cable speaker cables (with locking gold plated banana plugs). I am fairly certain I've used welders with smaller cables.

        (In my defence, I bought those as a teenager in the late 80s. I am not so easily marketed to with snake oil these days. I hope.)

        (On the other hand, I really like the idea of a reliably stable plus and minus 70V or maybe 100V DC power supply to my house. That'd make audio power amplifiers much easier and lighter...)

  • bandrami 8 hours ago |
    I stg if I see the kids talk about Westinghouse being batterymogged I'm leaving the Internet
  • otterley 8 hours ago |
    DC power has been an option for datacenter equipment since I was a young lad racking and stacking hardware. Cisco, Dell, HPE, IBM, and countless others all had DC supply options. Same with PDUs. What’s old is new again.

    See e.g. https://www.dell.com/support/kbdoc/en-us/000221234/wiring-in...

    • bluGill 7 hours ago |
      48vdc was common in phone exchanges. They filled the basement with lead-acid batteries and to could run without the grid for a couple weeks. In turn the phone was 99.999% reliable for decades.
      • mjuarez 7 hours ago |
        Not to be _that_ guy, but it was technically -48V DC.

        Honestly, that was pretty surprising to me when I had to work with some telco equipment a couple of decades ago. To this day, I don't think I've encountered anything else that requires negative voltage relative to ground.

        • yostrovs 7 hours ago |
          Check out older English cars.
        • bluGill 7 hours ago |
          positive ground used to be in all cars. When they went from 6 volts to 12 the disadvantages became appearant fast and so everyone went negative ground then (mid 1950s). I am not clear why positive ground was bad (maybe corrosion?)
        • servo_sausage 7 hours ago |
          Is that something other than a labelling convention? Is ground actually connected to a earth stake?
          • CamperBob2 7 hours ago |
            Cathodic protection against corrosion was the goal of using -48V, in the telcos' case.
            • myself248 5 hours ago |
              And the telegraph lines before that.
        • jacquesm 6 hours ago |
          Yes, and that tiny little difference can cost you a lot of expensive gear if you run it off the battery and plug in a serial port or something like that. You'll also learn first hand what arc welding looks like without welding glass.
        • SAI_Peregrinus 5 hours ago |
          Lots of amplifier circuits need a bipolar supply: both positive and negative voltages with respect to ground.
        • aidenn0 5 hours ago |
          RTL and DTL both needed negative-voltage relative to ground, as do many analog circuits.
        • em3rgent0rdr 5 hours ago |
          Some old guitar effects used -9V DC.[1] And the convention with guitar effects power adapter is the barrel is center negative (which is motivated with facilitating easy wiring of the socket's switch to connect to a 9V battery inside).

          [1] https://www.analogisnotdead.com/article26/what-is-going-on-w...

        • HWR_14 3 hours ago |
          Can you explain why it's -48 VDC as opposed to 48 VDC with the + and - inputs mislabeled?
      • divbzero 7 hours ago |
        Interesting, so this is why the phone line still worked when power was out across the whole town.
      • MathMonkeyMan 7 hours ago |
        Yeah I always heard that the phone lines carried their own power, and in Florida the phones did keep working when the power went out, but I never knew why.

        So the grid was always charging up the lead acid batteries, and the phone lines were always draining them? Or was there some kind of power switching going on where when the grid was available the batteries would just get "topped off" occasionally and were only drained when the power went out?

        • bluGill 7 hours ago |
          Grid charging batteries, phone draining them as I understand. Of course there were switches all over the us so I can't make blanket claims but from what I hear that was normal.
        • pocksuppet 6 hours ago |
          The phone grid predated the electrical grid. There was no other choice for power.

          Actually, there was one. Even earlier phones had their own power. A dry-cell battery in each phone, and every 6 months, the phone company would come around with a cart and replace everyone's battery. Central battery was found to be more convenient, since phone company employees didn't have to go around to everyone's site. Central offices could economize scale and have actual generators feeding rechargeable batteries.

        • qingcharles 5 hours ago |
          It's a pretty decent chunk of power down a POTS cable too, as it was designed to ring multiple big chunky metal bells in the days of yore.

          I was wiring in a phone extension for my grandma once as a boy and grabbed the live cable instead of the extension and stripped the wire with my teeth (as you do). I've been electrocuted a great number of times by the mains AC, but getting hit by that juicy DC was the best one yet. Jumped me 6ft across the room :D

          • rdtsc 5 hours ago |
            The teeth. Yikes! But yeah, I remember having the rotary phone disassembled and touching the wires adjusting something when a ring came. Gave me enough of a jolt to remember.
          • elcritch an hour ago |
            I discovered the same exact thing wiring a second phone line to my bedroom as a teenager. I jumped into a pile of fiberglass insulation! :/
      • idiotsecant 6 hours ago |
        I still have a bunch of 48vdc comms gear in my powerplant.
        • beAbU an hour ago |
          Why do you have a powerplant?
      • tverbeure 6 hours ago |
        -48V! :-)
    • _fizz_buzz_ 5 hours ago |
      Obviously 48VDC has been around and internally they will probably still step down to 48V. But these 48V islands are nowadays inter connected by regular AC grid. They want to replace that interconnection with a 800VDc bus. I kind of assume they chose 800vdc because there are already bunch of stuff available from EVs which also have 800vdc battery packs now.
      • 15155 3 hours ago |
        They chose 800VDC because it's a convenient multiple that is the peak possible with a two-level 650V (probably GaN) FET arrangement.
  • stego-tech 8 hours ago |
    I've been hearing this line for over a decade, now. "Immersion cooling will make data centers scale!" "Converting to DC at the perimeter increases density!"

    Yes, of course both of those things are true, and yes, some data centers do engage in those processes for their unique advantages. The issue is that aside from specialty kit designed for that use (like the AWS Outposts with their DC conversion), the rank-and-file kit is still predominantly AC-driven, and that doesn't seem to be changing just yet.

    While I'd love to see more DC-flavored kit accessible to the mainstream, it's a chicken-and-egg problem that neither the power vendors (APC, Eaton, etc) or the kit makers (Dell, Cisco, HP, Supermicro, etc) seem to want to take the plunge on first. Until then, this remains a niche-feature for niche-users deal, I wager.

    • otterley 7 hours ago |
      Those vendors all have DC power supply options, to my knowledge. It’s hardly new; early telco datacenters had DC power rails, since Western Electric switching equipment ran on 48VDC.

      https://www.nokia.com/bell-labs/publications-and-media/publi...

      • stego-tech 7 hours ago |
        That’s just it though, telco DCs != Compute DCs. Telcos had a vested interest in DC adoption because their wireline networks used it anyway, and the fewer conversions being done the more efficient their deployments were.

        Every single DC I’ve worked in, from two racks to hundreds, has been AC-driven. It’s just cheaper to go after inefficiencies in consumption first with standard kit than to optimize for AC-DC conversion loss. I’m not saying DC isn’t the future so much as I’ve been hearing it’s the future for about as long as Elmo’s promised FSD is coming “next year”.

        • jacquesm 6 hours ago |
          I think the real reason is because battery power didn't have to be converted twice to be able to run the gear in case of an outage, so you'd get longer runtime in case of a power failure, and it saves a bunch of money on supplies and inverters because you effectively only need a single giant supply for all of the gear and those tend to be more efficient (and easier to keep cool) than a whole raft of smaller ones.
    • arijun 7 hours ago |
      Surely if it makes sense for the big players, they will do it, and then the benefits will trickle down to the rest? Like how Formula 1 technology will end up in consumer vehicles.
    • gizmo686 7 hours ago |
      At least for servers, power supplies are highly modular. It just takes 1 moderately sized customer to commit to buying them, and a DC module will appear.

      Looking at the manual for the first server line that came to mind, you can buy a Dell PowerEdge R730 today with a first party support DC power supply.

  • hristov 7 hours ago |
    It is absolutely stupid to talk about this as edisons revenge. If Tesla had the modern high power transistors needed to get high voltage dc out of the ac produced from a spinning turbine he would be all for high voltage dc too. Tesla understood that high voltage was needed for efficient long range transmission. He also understood that transformers were the inly remotely efficient way to climb up to and down from these high voltages. And transformers only work with ac. So he designed an ac system and even designed some better transformers for it.

    If there was anything like a high power transistor back then he would have used that. High power transistors that are robust enough to handle the grid were designed inly recently over 100 years after the tesla/edison ac/dc argument.

    • arijun 7 hours ago |
      Also, if anything would have been Edison's revenge it would have been HVDC, where they're sending power long distances with DC. (But as you said, even there it wouldn't make a ton of sense, since they were arguing in a different era).
      • themafia 6 hours ago |
        The two primary reasons to do that are to allow the intertie of two AC grids that are not otherwise synchronized, and to take advantage of "earth return" paths when necessary to double the capacity of the line. The latter you may need to consider just to make the line cost effective over an equivalent AC span.
    • bluGill 7 hours ago |
      Tesla also design the modern induction motor which needs ac. Though these days we often run them on a phase generator which has a dc step.
    • jacquesm 7 hours ago |
      Agreed, for the IEEE to go down this route is more than a little weird.
    • Georgelemental 6 hours ago |
      It's just a fun title, you are overthinking it
    • chrneu 6 hours ago |
      the internet really needs to stfu about tesla and get over that oatmeal comic that spawned a billion internet myths. dude was a decent inventor but suffered from chronic mental health issues and, in his lifetime, wasted so much time/energy/money and burned so many bridges with his horrible attitude. there's a reason most people didnt like him in his day, he was a depressed asshole who alienated everyone around him, and yes I know he was likely gay in a time when that wasn't cool. the fact still remains; his inventions are massively overblown by internet nerds.

      the podcaster Sebastian Major from "Our Fake History" did a looonnngg patreon episode on tesla and debunked most of the weird myths around tesla. Sebastian doesn't have a vendetta or anything, it's just amazing how much of the Tesla stuff is just nonsense or is viewed through a very weird bias nowadays. Major also briefly touches on the weird Edison stuff and how the internet has twisted Edison into a villain.

      • anonymousiam 5 hours ago |
        Tesla was an outstanding technologist, but a poor businessman. He had a "vision" (actually more than one) about how his ideas could transform the world. Some of his ideas were amazing, but he was swindled out of his patents because the investors knew he had a passion and wanted to see them in use. The polyphase AC motor or fluorescent light bulb could have made him millions.

        IMHO, the vision he had about universal free electricity (transmitted wirelessly) was the dumbest. It was a novel idea, and he invested a lot (his time and other people's money) in it. The problem with his idea is that there was no way to monetize it (and profit from it). (There were also the technical issues of the power loss over distance (1/R^2), the harm to the environment, and the interference with radio communications.)

        Edison was quite a villain. He stole many of his "inventions", and orchestrated a PR campaign against Tesla touting the "evils" of AC power. AFAIK, the electric chair was either invented or inspired by him.

        I know these things because I've read many books on various topics related to Tesla, and all of this knowledge predates the Internet.

        • HWR_14 3 hours ago |
          Edison did not invent the electric chair. When the inventors were trying to choose between using AC or DC he helped them decide on AC as part of his PR campaign.
        • fsh 3 hours ago |
          Essentially none of this is true. The war of the currents was between Edison and Westinghouse, not Tesla. Tesla's downfall was that he turned into a crackpot who rejected modern science, such as Maxwell's equations, and started defrauding investors. Edison was an outspoken opponent of the death penalty, and the electric chair used AC simply because it is much more deadly.
      • aaronbrethorst 4 hours ago |
        We’re talking about Nikola Tesla, not Elon Musk, and I don’t think Musk is gay.
        • beAbU an hour ago |
          I think you need to read the post you are responding to again.
          • aaronbrethorst an hour ago |
            Whoosh!
    • teleforce 5 hours ago |
      >It is absolutely stupid to talk about this as edisons revenge. If Tesla had the modern high power transistors needed to get high voltage dc out of the ac produced from a spinning turbine he would be all for high voltage dc too.

      This!

      The soon people realized these facts the better. The pervasive high rise buildings did not happen before the invention of modern cranes.

      Exactly twenty years ago I was doing a novel research on GaN characterization, and my supervisors made a lot money with consulations around the world, and succesfully founded govt funded start-up company around the technology. Together with SiC, these are the two game changing power devices with wideband semiconductor technology that only maturing recently.

      Heck, even the Nobel price winning blue LED discovery was only made feasible by GaN. Watch the excellent video made by Veritasium for this back story [1].

      [1] Why It Was Almost Impossible to Make the Blue LED:

      https://youtu.be/AF8d72mA41M

      • mcbishop 5 hours ago |
        I've heard the EV charging has played a big role in the maturation of GaN / SiC.
        • teleforce 5 hours ago |
          Yes, EV and high frequency electronics (microwave, mmWave, photonics) that require very fast switching capability.
          • UltraSane 4 hours ago |
            And military radars love GaN
      • jibal 4 hours ago |
      • ta9000 3 hours ago |
        Does that mean when we run out of Ga there are no more LED TVs?
    • bryanrasmussen 4 hours ago |
      sure, and also Montezuma didn't actually plan on diarrhea ruining people's vacations, but vernacular usage being what it is we have the phrase Montezuma's revenge.

      I only found Edison in the headline, I didn't find it anywhere in the body, nor did I find Tesla. Glancing through the article it almost seems like someone tried to make a catchy headline to get clicks.

    • fsh 3 hours ago |
      It was Westinghouse who pushed the AC grid against his rival Edison's DC approach. Tesla was a minor figure working for both of them for a bit.
  • sghiassy 7 hours ago |
    I’ve always wondered about these new High-Voltage DC (HVDC) transmission lines.

    I always thought AC’s primary benefit was its transmission efficiency??

    Would love to learn if anyone knows more about this

    • cjbgkagh 7 hours ago |
    • adgjlsfhk1 7 hours ago |
      AC is less efficient than DC at a given voltage. The advantage of AC is that voltage switching is cheap, easy and efficient. Switching DC voltage is way harder, more expensive, and less efficient. However the switching costs are O(1) and the transmission losses are O(n) so for some distance (currently somewhere around 500 km) it's worth paying the switching cost to get super high voltage DC. The big thing that's changed in the last ~30 years is a ton of research into high voltage transistors, and fast enough computers to do computer controlled mhz switching of giant high power transistors. These new super fancy switching technologies brought the switching costs down from ludicrous to annoyingly high.
      • arijun 7 hours ago |
        > AC is less efficient than DC at a given voltage

        To expand on this, a given power line can only take a set maximum current and voltage before it becomes a problem. DC can stay at this maximum voltage constantly, while AC spends time going to zero voltage and back, so it's delivering less power on the same line.

        • adgjlsfhk1 6 hours ago |
          this iirc is the smallest of 3 problems. the other 2 are skin effect (AC wires only store power on the outside of the wire) and capacitive effects (a write running parallel to the ground is a capacitor and AC current is equivalent to constantly charging and discharging the capacitor)
        • manwe150 6 hours ago |
          That’s true, but my understanding is the main contributor is skin effect, since AC travels only on the surface of the wire, while DC uses the whole area, resulting in lower resistance loss (https://en.wikipedia.org/wiki/Skin_effect)
        • adiabatichottub 5 hours ago |
          Maybe if by "same voltage" we mean DC voltage the same as AC peak voltage. When we talk about AC voltage we are referring to root-mean-square (RMS) voltage. It's kind of like saying the average, though for math reasons the average of an unbiased sine wave is 0. Anyhooo, 1 VRMS into a load will produce the same power as 1VDC. If AC delivered less power than DC at the same voltage then life would be very confusing.
    • cogman10 7 hours ago |
      The primary benefit of AC is it's really easy to change the voltage of AC up or down.

      The transmission efficiency of AC comes from the fact that you can pretty trivially make a 1 megavolt AC line. The higher the voltage, the lower the current has to be to provide the same amount of power. And lower current means less power in line loss due to how electricity be.

      But that really is the only advantage of AC. DC at the same voltage as AC will ultimately be more efficient, especially if it's humid or the line is underwater. Due to how electricy be, a change in the current of a line will induce a current into conductive materials. A portion of AC power is being drained simply by the fact that the current on the line is constantly alternating. DC doesn't alternate, so it doesn't ever lose power from that alternation.

      Another key benefit of DC is can work to bridge grids. The thing causing a problem with grids being interconnected is entirely due to the nature of AC power. AC has a frequency and a phase. If two grids don't share a frequency (happens in the EU) or a phase (happens everywhere, particularly the grids in the US) they cannot be connected. Otherwise the power generators end up fighting each other rather than providing power to a load.

      In short, AC won because it it was cheap and easy to make high voltage AC. DC is comming back because it's only somewhat recently been affordable to make similar transformations on DC from High to low and low to high voltages. DC carries further benefits that AC does not.

    • prezk 7 hours ago |
      Important factor is that AC at given nominal voltage V swings between 1.41V and -1.41V, so it requires let's say 40% better/thicker insulation than the equivalent V volts DC line. This is OK for overhead lines (just space the wires more) but is a pain for buried or undersea transmission lines; for that reason, they tend to use DC nowadays.

      BTW, megavolt DC DC converters are a sign to behold: https://en.wikipedia.org/wiki/File:Pole_2_Thyristor_Valve.jp...

    • topspin 6 hours ago |
      > I always thought AC’s primary benefit was its transmission efficiency??

      There are many factors involved, and "efficiency" is only one. Cost is the real driver, as with everything.

      AC is effective when you need to step down frequently. Think transformers on poles everywhere. Stepping down AC using transformers means you can use smaller, cheaper conductors to get from high voltage transmission, lower voltage distribution and, finally lower voltage consumers. Without this, you need massive conductors and/or high voltages and all the costs that go with them.

      AC is less effective, for instance, when transmitting high power over long, uninterrupted distances or feeding high density DC loads. Here, the reactive[1] power penalty of AC begins to dominate. This is a far less common problem, and so "Tesla won" is the widely held mental shortcut. Physics doesn't care, however; the DC case remains and is applied when necessary to reduce cost.

      [1] https://en.wikipedia.org/wiki/Electrical_reactance

  • umvi 7 hours ago |
    I don't understand why new houses don't just have one high quality AC/DC converter so you can just use LED lighting without every bulb needing its own AC/DC converter. I imagine the light bulb cartel wouldn't really like that.
    • bluGill 7 hours ago |
      It wouldn't work. leds need low voltages, meaning massive wires. you can run the voltage change on ac or dc. Ac just needs a few capacters to smooth the wave out.
    • throw0101d 7 hours ago |
      > I don't understand why new houses don't just have one high quality AC/DC converter so you can just use LED lighting without every bulb needing its own AC/DC converter.

      IEEE 802.3bt can deliver up to 71W at the destination: just pull Cat 5/6 everywhere.

      * https://en.wikipedia.org/wiki/Power_over_Ethernet#Standard_i...

      * https://www.usailighting.com/poe-lighting

      • elcritch 39 minutes ago |
        And pay $60 per Ethernet POE+ light bulb.
    • fortran77 7 hours ago |
      Do you want your house to burn down? Lower voltages for LED lights mean higher current.
      • bigiain 6 hours ago |
        That's traded off against the increase efficiency of LED lighting, at least compared to incandescent lighting. An LED "equivalent replacement" for a typical incandescent globe is down around 1/10th of the power. A 7Watt LED bulb is typically marketed as "60W equivalent". If that configured as a bunch of LEDs in series (or series/parallel) that need 12VDC, it's right about the same current draw as the 120V 60W incandescent equivalent. (Or perhaps double the current for those of us who get 220VAC out of our walls.)

        (Am I just showing my age here? How many of you have ever bought incandescent globes for house lighting? I vaguely recall it may be illegal to sell them here in .au these days. I really like quartz halogen globes, and use them in 4 or 5 desk lamps I have, but these days I need to get globes for em out of China instead of being able to pick them up from the supermarket like I could 10 or 20 years ago.)

    • Majromax 7 hours ago |
      With modern technologies, that's power over ethernet or USB-C. Other comments in this thread point out that the telephone service also routinely used 48V for the ring signal.

      However, higher DC voltage is riskier, and it's not at all standard for electrical and building code reasons. In particular, breaking DC circuits is more difficult because there's no zero-crossing point to naturally extinguish an arc, and 170V (US/120VAC) or 340V (Europe/240VAC) is enough to start a substantial arc under the right circumstances.

      Unfortunately for your lighting, it's also both simple and efficient to stack enough LEDs together such that their forward voltage drop is approximately the rectified peak (i.e. targeting that 170/340V peak). That means that the bulb needs only one serial string of LEDs without parallel balancing, making the rest of the circuitry (including voltage regulation, which would still be necessary in DC world) simpler.

    • fragmede 7 hours ago |
      because shorts and voltage loss are a real issue at that scale.
    • gizmo686 6 hours ago |
      LED light bulbs exist exclusively for compatibility with Edison sockets. Every LED fixture I have seen had a single transformer for the entire fixture; and that transformer was reasonably separate from the LEDs themselves.
    • ianburrell 5 hours ago |
      What voltage do you use? Most DC stuff wants low voltage (5-48V), but appliances need higher voltage like AC-level to get enough power over existing wiring. The result is DC-DC converters every place that have transformers now.

      The gain from DC-DC converters is small and DC devices are small part of usage compared appliances. There is no way will pay back costs of replacing all the appliances.

    • amluto 4 hours ago |
      Every decent LED would then need … a switching power supply. LEDs are current-driven devices, and you get the best efficiency if you use an actual current-controlled supply. And those ICs are very, very cheap now.

      The part that would genuinely be cheaper is avoiding problematic flicker. It takes a reasonably high quality LED driver to avoid 120Hz flicker, but a DC-supplied driver could be simpler and cheaper.

  • adrr 7 hours ago |
    Our houses should be DC. So wasteful to have all these bricks to change to AC to DC.
    • bandrami 7 hours ago |
      I've worked overseas a lot and one thing that's really different from 2 decades ago is that I simply don't need a step-down transformer anymore because every single thing I plug in converts to DC (or otherwise accepts dual-voltage) anyways. So I have a giant collection of physical plug adapters because every device I use just needs to fit into the socket and takes care of it from there.

      (My stand mixer is the lone sad exception)

      • 747fulloftapes 4 hours ago |
        Agreed!

        I spent a few years getting flown out around the world to service gear at different datacenters. I learned to pack an IEC 60320 C14 to NEMA 5-15R adapter cable and a dumb, un-protected* NEMA 5-15R power strip. While on-site at the datacenters, an empty PDU receptacle was often easy to find. At hotels, I'd bring home a native cable borrowed from or given to me by the native datacenter staff or I'd ask the hotel front desk to borrow a "computer power cable," (more often, I'd just show them a photo) and they generally were able to lend me one. It worked great. I never found a power supply that wasn't content with 208 or 240V.

        Example adapters: https://www.amazon.com/dp/B0FD7PHB7Y or https://www.amazon.com/dp/B01IBIC1XG

        *: Some fancier power strips with surge suppression have a MOV over-voltage varistor that may burn up if given 200V+, rendering the power strip useless. Hence, unprotected strips are necessary.

    • ericd 7 hours ago |
      Something to consider, and something I got a vivid demonstration of while playing with solar panels, DC arcs aren't self-extinguishing, unlike AC arcs. At one point I stuck a voltage probe in, and the arc stuck with it as I pulled the probe away. It also vaporized the metal tip of the probe.

      My understanding is that DC breakers are somewhat prone to fires for this reason, too.

      • bigiain 7 hours ago |
        Heh - I vaporised a fairly large soldering iron tip (probably 4mm copper cylindrical bar?), when I fucked up soldering a connector to a big 7 cell ~6000mAHr LiPo battery and shorted the terminals. Quite how I didn't end up blind or in hospital I don't know. It reinforced just how much respect you need to pay to even low-ish voltage DC when the available current was likely able to exceed 700A by a fair margin momentarily. I think those cells were rated at 60C continuous and 120C for 5 seconds.
        • ericd 7 hours ago |
          heh man, I'm glad you got out of that easy, I definitely wore safety glasses 100% of the time after my experience. I think a lifetime of experience with dangerous wall outlets and harmless little 1.5V/9V DC cells teaches us the wrong lessons about DC safety. I've since heard stories of wrenches exploding when they fall across EV high voltage battery terminals. Wrenches aren't supposed to be explosive.

          The electricians I was working with also told me stories about how with the really big breakers, you don't stand in front of it when you throw it, because sometimes it can turn into a cloud of molten metal vapor. And that's just using them as intended.

          • bluGill 6 hours ago |
            Amps - the old 48vdc telco data centers vaporized wrenchs once in a while.
          • jacquesm 6 hours ago |
            Those harmless 9V DC cells can do a lot of damage if you use them right.
          • scheme271 6 hours ago |
            A bunch of those big breakers require two people. One person in a flash suit and another with a 2m long pole around the first person. That way if an arc flash happens, the second person can yank the first person to safety without also getting hurt.
            • pocksuppet 6 hours ago |
              Why don't they use the pole to flip the breaker from 2m away?
              • defrost 6 hours ago |
                Ruins the fun and interrupts instilling respect deep into the bones of interns.

                Allegedly

                While on "work experience" from high school I was put on washing power lines coming straight out of the local power station near the ocean - lots of salt buildups to clear.

                Same deal, flashover suits and occasional arcs .. and much laughter from the ground operators who drifted the work bucket close.

        • jacquesm 6 hours ago |
          You got super lucky.
          • bigiain 6 hours ago |
            Yep. Super super lucky. I suspect my reading glasses are the only reason I can still see anything.
            • jacquesm 6 hours ago |
              I have a couple of those narrow escapes one of which led me to put a significant chunk of Eastern Amsterdam out of power. Another involved Beryllium oxide. 9 lives are barely enough.
              • bigiain 6 hours ago |
                I would read that book...
                • jacquesm 5 hours ago |
                  'Stupid stuff I've done and survived'...
              • swamp_donkey 3 hours ago |
                Ah! Perhaps you are a member of the gigawatt club? Eligible for entry once you have accidentally tripped off 1000 MW of load or generation! No sweeping that under the table
      • toast0 5 hours ago |
        > DC arcs aren't self-extinguishing, unlike AC arcs. At one point I stuck a voltage probe in, and the arc stuck with it as I pulled the probe away. It also vaporized the metal tip of the probe.

        It would have self-extinguished if you waited long enough for the probe to vaporize.

    • kccqzy 7 hours ago |
      That’s actually a recent phenomenon. Before the age of electronics most household appliances either worked with AC or DC equally well (like incandescent bulbs) or worked well with AC only given the technology at the time (think anything with a motor, fans, HVAC compressors etc).
      • analog31 7 hours ago |
        Taking it to an extreme, the house I lived in while in grad school had wall lamp fixtures that doubled as electric and gas lamps. At some point I imagine it would have been possible to choose between using electric or gas by either flipping the switch or turning a valve. They said "Edison Patent" on them. We could have lit the house on AC, DC, or gas.

        Thinking about the failure modes gave me the heebie jeebies, but the gas had been disconnected ages prior.

        • jazzyjackson 6 hours ago |
          It’s kind of fun that light switches predate electricity. I think you used to turn a key, I guess you were turning a valve? Now that I think of it using a key to operate a valve makes a lot of sense but you don’t see it too often, well, I guess you want to turn things off without needing to find a key…
        • eszed 2 hours ago |
          I lived in a 19th century house in San Francisco that had gorgeous plaster work medallions on the ceilings - think cherubs and fruits - in the middle of which were the light fixtures. One day my dumb-ass flatmate made an ill-advised attempt to DIY his light fixture and cracked the still-active gas line embedded in the ceiling. Sometime in the 1920s - the date was printed on a sticker in the electrical panel - when they electrified the house, they'd wrapped the electrical wires around the gas pipes, and left them otherwise in situ. Crazy stuff.
    • torginus 7 hours ago |
      I've had discussed with people familiar with the matter, and they convinced me its really not worth it for many reasons, the main one being safety - DC arcs are self sustaining - AC voltage constantly goes to zero, so if an arc were to form, it gets auto extinguished when the voltage drops. With DC this never happens, meaing every switch or plug socket can create this nice long arcs and is a potential fire hazard.
      • adiabatichottub 7 hours ago |
        Really depends on what we're talking about. A lot of electrical safety equipment has a DC rating, usually something like 90VDC/300VAC. Also, most DC equipment just isn't going to have the stored energy to generate a big arc. Well, except batteries, and we're already piling them all around us.
        • torginus 6 hours ago |
          I mean it depends, but for dual rated stuff has both a voltage and current limit, both of which are way lower. Like typically a 230V/20A AC switch can switch 24VDC/2A. And the energy is not in the equipment, its in the mains (or batteries like you said, or PV panels)
          • adiabatichottub 6 hours ago |
            Right, but that's why I mentioned safety equipment. Your common DIN-mount UL-489 branch circuit breaker will be rated for the same trip current, same short circuit current rating (SCCR), but lower voltage. So you can use the same wiring and breakers as you might have with AC and your 48V battery bank won't vaporize the $5 hardware store toggle switch that somehow became a shunt.
            • torginus 15 minutes ago |
              I mean, most AC circuit breakers use electromagnets to trip on overcurrent (as well as bimetallic strips using thermal methods for sustained high current).

              Electromagnets dont work for DC, so your breaker will never trip. For thermal protection, you need current, so that checks out, and it would make sense for it to be rated under 50V as thats considered the highest voltage thats not life threatening on touch.

              PV Batteries in general have a very high current (100s of A) at ~50Vish volts, so I dont think there's a major usecase for using household breakers for them.

              Im still not getting your point BTW, switches and breakers are two separate things, with different workings, and household (and datacenter) DC would be I think around 400ish V, which is a bit higher than the peak voltage of AC, but still within the arc limits of household wiring (at least in 230V countries).

              The advantage of DC is that you use your wiring more efficiently as the mean and peak wattage is the same at all times. Going with 48V would mean high resistive losses.

      • jacquesm 6 hours ago |
        The 'what is safer' question for DC and AC at the same effective current and power has a mixed set of answers depending on conditions. For instance, DC is more likely to cause your muscles to contact and not let go (bad), but AC is more likely to send your heart into ventricular fibrillation (sp?, also bad).

        AC arcs are easier to extinguish than DC arcs, but DC will creep much easier than AC and so on.

        From a personal point of view: I've worked enough with both up to about 1KV at appreciable power levels and much higher than that at reduced power. Up to 50V or so I'd rather work with DC than AC but they're not much different. Up to 400V or so above that I'd much rather have AC and above 400V the answer is 'neither' because you're in some kind of gray zone where creep is still low so you won't know something is amiss until it is too late. And above 1KV in normal settings (say, picture tubes in old small b&w tvs and higher up when they're color and larger) and it will throw you right across the room but you'll likely live because the currents are low.

        HF HV... now that's a different matter and I'm very respectful of anything in that domain, and still have a burn from a Tronser trimmer more than 45 years after it happened. Note to self: keep eye on SWR meter/Spectrum analyzer and finger position while trimming large end stages.

        • Tempest1981 3 hours ago |
          > DC will creep much easier than AC

          Can you say more about "creep"? Is the resistance changing? Or is material actually migrating?

          Also curious why it's worse using DC.

    • bigiain 7 hours ago |
      Sure, maybe?

      If your house gets 800V DC you're still gonna need "bricks" to convert that to 5VDC of 12VDC (or maybe 19VDC) that most of the things that currently have "bricks" need.

      And if your house gets lower voltage DC, you're gonna have the problem of worth-stealing sized wiring to run your stove, water heater, or car charger.

      I reckon it'd be nice to have USB C PD ports everywhere I have a 220VAC power point, but 5 years ago that'd have been a USB type A port - and even now those'd be getting close to useless. We use a Type I (AS/NZS 2112) power point plug here - and that hasn't needed to change in probably a century. I doubt there's ever been a low voltage DC plug/socket standard that's lasted in use for anything like that long - probably the old "car cigarette lighter" 12DC thing? I'm glad I don't have a house full of those.

    • jwilliams 7 hours ago |
      There are niches where DC makes sense - low-voltage lighting, USB/LED ecosystems.

      Once you get into higher power (laptops and up), switching and distribution get harder, so the advantages fade.

      For bigger appliances (fridge, etc), AC is fine + practical.

      • adiabatichottub 6 hours ago |
        Your modern fridge is probably going to have an inverter-driven motor, so you're right back to using DC.
        • adrr 6 hours ago |
          All modern appliances and HVACs are using inverter drive motors for efficiency. Brushless DC motors are more efficient though.
          • userbinator 6 hours ago |
            "Brushless DC motors" are actually just AC synchronous motors.
    • epx 7 hours ago |
      Having a single big DC converter at a home would help a lot with power factor (LED lamps connected directly to AC have terrible power factor).
    • Mistletoe 7 hours ago |
      Modern bricks really aren’t that inefficient though. An Apple charger is like 90% efficient. A DC to DC converter is about that efficient or worse.
      • catlikesshrimp 6 hours ago |
        The power adapters became so efficient that we have to transition to wireless charging to keep it down

        The irony...

    • flowerthoughts 3 hours ago |
      I'm renovating a house, and have been considering 24V or 48V DC outlets in a few rooms. Semiconductors become more expensive above ~32V, so 24V might be the sweetspot.

      However, there's also PoE (24 or 48V!), so maybe that's the right approach. It's not like each outlet is going to run a heater anyway.

      • fc417fc802 an hour ago |
        Lower voltage makes voltage drop across the line proportionally worse. Depending on the purpose PoE is probably the way to go since the wiring and hardware is all standardized and safety certified.

        Unless you mean running AC and installing inverters in the wall? What is this even for? All my electronics are DC but critically they all require different voltages. The only thing I might benefit from would be higher voltage service because there are times that 15 A at 120 V doesn't cut it.

  • Aloisius 7 hours ago |
    This article seems to imply that 800V DC is high-voltage DC, but that seems quite low.
    • MathMonkeyMan 7 hours ago |
      Quite low compared to a power utility's HVDC, but quite high compared to the 5/12/24 V output of most AC/DC converters used for electronics.
    • bigiain 6 hours ago |
      I think there'a a regulatory "Low Voltage" definition of "below 50V", which has implications around whether you need to be a licensed electrician to install it or not. Anything above that is - for at least some purposes - considered "High Voltage".

      Other people, of course, have other definitions of high voltage:

      "This resonant tower is known as a Tesla coil. This particular one is just over 17 feet tall and it can generate about a million volts at 60,000 cycles per second."

      and:

      "This pulse forming network can deliver a shaped pulse of over 50,000 amps with a total energy of about 1,057 times the tower primary energy"

      https://www.youtube.com/watch?v=RoGbrgOhPes

  • KnuthIsGod 7 hours ago |
    Waiting for home DC.

    It is silly to have AC to DC converters in all of my wall connected electronics ( LED bulbs, home controller, computer equipment etc )

    • jacquesm 7 hours ago |
      Not going to happen. For the same reason that the US never converted to a higher domestic voltage even though there are many practical advantages. The transition from one system to another at the consumer level would be terrible, even if there would be some advantage (and I'm not sure the one you list is even valid, you'd get DC-DC converters instead because your consumers typically use a lower voltage than the house distribution network powering your sockets) it would be offset by the cost of maintaining two systems side by side for decades.

      You could wire your house for 12, 24 or 48V DC tomorrow and some off-grid dwellers have done just that. But since inverters have become cheap enough such installations are becoming more and more rare. The only place where you still see that is in cars, trucks and vessels.

      And if you thought cooking water in a camper on an inverter is tricky wait until you start running things like washing machines and other large appliances off low voltage DC. You'll be using massive cables the cost of which will outweigh any savings.

      • manwe150 6 hours ago |
        I suppose that still begs the question somewhat, since the US does have 240V (2 phase) already driving many appliances. Why hasn’t it ever become standard for luxury kitchens to have a European-style outlet for use with a European kettle? I know the US already has a different 240V plug shape, so it might have to be an unlicensed installation, but surely someone wanted hot tea faster and did that calculus before?
        • jacquesm 6 hours ago |
          Well, as you say, it would not be according to code and the insurance company might have something to say about it. It's also single phase but not quite the way you do it in the USA, it would be a neutral and a phase whereas in the USA I think it is 2x110. Finally, it's 50 Hz rather than 60 which would work fine for resistive loads but not so well for inductive ones such as transformers and motors.

          In all likely not worth the trouble. When I moved to Canada I gave away most of my power tools for that reason and when I moved back I had to do that all over again.

          • aidenn0 5 hours ago |
            > In all likely not worth the trouble. When I moved to Canada I gave away most of my power tools for that reason and when I moved back I had to do that all over again.

            If you ever have to do it again, you can probably get a transformer rated high enough for power-tools for cheaper than replacing all of your power tools.

        • ianburrell 6 hours ago |
          You can run 240V circuit to kitchen for kettle and put in NEMA 6 outlet. But few people care about fast boil and importing European kettle. Most people use the microwave or stovetop, and 120V kettles are fine in most cases. It will never become a standard thing.
        • tbrownaw 5 hours ago |
          > I know the US already has a different 240V plug shape, so it might have to be an unlicensed installation, but surely someone wanted hot tea faster and did that calculus before?

          How expensive would a proper AC->DC->AC brick for that power level be?

          • jacquesm 5 hours ago |
            Not so simple, you'd have to use a 'drier' or 'welder' socket for that otherwise you won't have enough power. A single circuit in Europe is 240V 16A or 3840W!

            A pure sinewave inverter for that kind of power is maybe 600 to 1000 bucks or so, then you'd still need the other side and maybe a smallish battery in the middle t stabilize the whole thing. Or you could use one of those single phase inverters they use for motors.

        • jcalvinowens 5 hours ago |
          I wired a UK kettle to an unused 240V range outlet in the US once. It was amazing, boiled a liter of water in just under a minute. Obviously kinda sketchy.
          • jacquesm 5 hours ago |
            That's more like it :)
        • vessenes 4 hours ago |
          Most important comment here!! I would love to buy like a 6kw battery induction kettle for the states. As far as I can tell, they don’t exist.
        • fc417fc802 2 hours ago |
          Ahckhually US residential is split single phase, not two phase. https://en.wikipedia.org/wiki/Split-phase_electric_power

          I think the answer to your question is that it mostly doesn't matter for personal mug size quantities of hot water and if it does matter to you there are readily available competing options such as dedicated taps for your kitchen sink.

          Perhaps the biggest reason is that a traditional kettle on any half decent electric range will match if not exceed the power output of any imported electric kettle. Many even go well beyond that with one burner marked "quick boil" or similar.

      • SoftTalker 4 hours ago |
        I'm not sure it's likely, but I could see DC lighting start to happen in new construction. Have a single AC-to-DC converter off the main service entrance that powers hard-wired LED lighting fixtures in the house. Would probably be better than running the individual (and usually very low quality) converters in dozens of standard LED light bulbs. Would need to be standardized, codified, etc. so probably not happening soon.
      • wincy 3 hours ago |
        I just wish I could run my air conditioner and my desktop computer at the same time without flipping the breaker. The RTX 5090 is a space heater and will easily peg at the 600W it’s rated for, and so with that and an air conditioner window unit, I have to run a long cable from another unused room if I want to do anything that stresses the video card.
    • ternus 6 hours ago |
      The lesser-known instance of this is RV power. When you're running off small batteries and solar, you want to make the best use of the watt-hours you have, and that means avoiding the DC-to-AC-to-DC loop wherever possible. So you run 12V (or in newer models, higher voltage) versions of everything, upconverting as necessary.
      • amluto 4 hours ago |
        I am really skeptical that 12VDC power distribution in RVs actually saves power compared to a high-quality (hah!) higher voltage AC or DC system. 12V is absurdly low and you can’t easily lose quite a few percent in resistive losses even with fairly large cables, and those large cables are quite unpleasant to work with and rather dangerous.
        • saltyoldman 4 hours ago |
          I tried using a microwave off the RV batteries, your inverter needs 4/0 cable. Very "fun".
    • scarecrowbob 6 hours ago |
      Well, having spent some time operating a 12VDC system last year when I moved into some shacks, I will say that I find it a lot more convenient to run 120VAC.

      I end up converting stuff anyhow, because all my loads run at different voltages- even though I had my lights, vent fan, and heater fans running on 12V I still ended up having to change voltages for most of the loads I wanted to run, or generate a AC to to charge my computer and run a rice cooker.

      Not to mention that running anything that draws any real power quickly needs a much thicker wire at 12V. So you're either needing to run higher voltage DC than all your loads for distribution and then lowering the voltage when it gets to the device, or you simply can't draw much power.

      Not that you can't have higher voltage DC; with my newer system the line from my solar panels to my charger controller is around 350VDC and I can use 10awg for that... but none of the loads I own that draw much power (saws, instapot, rice cooker, hammond organ, tube guitar amp) take DC :D

      • jazzyjackson 6 hours ago |
        Catch me wiring my house with 20V USBC ;)
    • est 6 hours ago |
      home appliances have lower voltage, like 12V or 5V. The wire loss and heat would be a problem.
    • hahn-kev 6 hours ago |
      It's called USB power delivery
  • skullone 6 hours ago |
    Transitioning? It already happened decades ago. Only smaller scale/generic or less proficient "we bought all Dell and HP" use AC. At large scale it's been a ton of DC for literally decades. And for 70 years in telco and network gear.
  • b00ty4breakfast 6 hours ago |
    They're still converting from AC to DC at the datacenter, it just isn't being stepped down at the perimeter. There is no transmission of HVDC going on. This isn't really Edison's revenge, more like his consolation price, ha!
  • neoCrimeLabs 5 hours ago |
    The datacenter I built in 2007 was DC.

    Many datacenters I'd been to at that point were already DC.

    Didn't think this was that new of a trend in 2026, but also acknowledge I did not visit more than a handful of datacenters since 2007.

    It just seemed like a undenyably logical thing to do.

  • Animats 5 hours ago |
    800V to each rackmount unit, with hot plugging of rack units? That's scary. The usual setup at this voltage is that you throw a hulking big switch to cut the power, and that mechanically unlocks the cabinet. But that's not what these people have in mind. They want hot-plugging of individual rackmount units.

    GE has a paper about the power conversion design, but it doesn't mention the unit to rack electrical and mechanical interface. Liteon is working on that, but the animation is rather vague.[2] They hint at hot plugging but hand-wave how the disconnects work. Delta offers a few more hints.[3] There's a complex hot-plugging control unit to avoid inrush currents on plug-in and arcing on disconnect. This requires active management of the switching silicon carbide MOSFETs.

    There ought to be a mechanical disconnect behind this, so that when someone pulls out a rackmount unit, a shutter drops behind it to protect people from 800V. All these papers are kind of hand-wavey about how the electrical safety works.

    Plus, all this is liquid-cooled, and that has to hot-plug, too.

    [1] https://library.grid.gevernova.com/white-papers-case-studies...

    [2] https://www.youtube.com/watch?v=CQOreYMhe-M&

    [3] https://filecenter.deltaww.com/Products/download/2510/202510...

    • rdtsc 4 hours ago |
      It is a pretty clever design

      > When it is detected that the PDB starts to detach from the interface, the hot-swap controller quickly turns off the MOSFET to block the discharge path from Cin to the system. After the main power path is completely disconnected, the interface is physically detached, and no current flows at this time

      > For insertion, long pins (typically for ground and control signals) make contact first to establish a stable reference and enable pre-insertion checks, while short pins (for power or sensitive signals) connect later once conditions are safe; during removal, the sequence is reversed, with short pins disconnecting first to minimize interference.

      • Animats 4 hours ago |
        Yes, I read that. There had better be a backup system. MOSFETs tend to fail ON, and there's a megawatt going into each rack.

        Somehow this seems the wrong approach to AI.

  • amluto 4 hours ago |
    I wonder how much of the benefit is simpler redundant power equipment. For AC, you have standby UPSes and line-interactive UPSes and frequency and phase synchronization. And everything needs a bit more hold-up time because, in case of failure, your new power supply might be at a zero crossing.

    For 800V DC, a simple UPS could interface with the main supply using just a pair of (large) diodes, and a more complex and more efficient one could use some fancy solid state switches, but there’s no need for anything as complex as a line-interactive AC UPS.

  • saltyoldman 4 hours ago |
    The large brick you have on all your tech when you plug it in is the converter. AC works great for some applications, none of them really technical in nature.